Im planning to run extension leads down to the back shed run a tent grow. I need to join a few togetjer to reach it, roughly 60metres. Do you think it will affect the equipment. I will be running 600watt hps 6 inch fan (200w)possibly more lights for a veg tent. Im going to tape and silicone joins for weatherproofing. For stealth it will be buried shallow. Mostly worried about the length, whats your thoughts/experience? Thanks

 

 

 

 

Posted from the OZ Stoners mobile app

Link to comment
Share on other sites

Biggest factor is the diameter of your wire in the extension leads... most cheapies are only using 1.0mmsquare wires which running anything more than low current will get real hot pretty quickly. If you're handy get some 2.5mm square 3 core wire and a male and female plug for either end and make your own extension lead.

 

Posted from the OZ Stoners mobile app

  • Upvote 1
Link to comment
Share on other sites

That's how much voltage drop between point a n point b

A better idea would be to run bigger cable with no joins n a small distribution board at the end ,point b with a circuit breaker n a few power points

Better safe than sorry

 

Posted from the OZ Stoners mobile app

Ok thanks micmac sounds a little complicated fir me to do and dont have the $to pay a spark to come do it. Might reconsider my options could possibly knock a soace together under the house where there are existong powerpoints but prob gonna look suss as fuck. Just moved here and sussing out my options. Thanks for the advice

 

 

Posted from the OZ Stoners mobile app

Link to comment
Share on other sites

Biggest factor is the diameter of your wire in the extension leads... most cheapies are only using 1.0mmsquare wires which running anything more than low current will get real hot pretty quickly. If you're handy get some 2.5mm square 3 core wire and a male and female plug for either end and make your own extension lead.

 

Posted from the OZ Stoners mobile app

That sounds doable, could i do that still with 4mm cable?

 

 

Posted from the OZ Stoners mobile app

Link to comment
Share on other sites

4mm will be perfect with a little sub board n 32amp mcb/rcd combo breaker with a few power points..you could go 6mm but would be a overkill

 

Posted from the OZ Stoners mobile app

thanks kalm might be a bit beyond me but will chat to a mate about it. Whats your thoughts on the male and female plig on a 4mm cable?

 

 

Posted from the OZ Stoners mobile app

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Restore formatting

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...

Important Information

By using the community in any way you agree to our Terms of Use and We have placed cookies on your device to help make this website better. You can adjust your cookie settings, otherwise we'll assume you're okay to continue.